How To reset PULSE COUNTER IN S800 DP840
Answers
I'm afraid you cannot change DP840 board settings in online mode (re-activate channel to reset pulse count).
In the control program you need provide logical pulse counter that accumulates pulses from a board channel.
Logical pulse counter can be reset by activating dedicated program input, button on interaction window or on operator display.
regards
greetings
yes , you can do Counter reset in both the DP840 and DP820 by doing the follwoign:
1-Counter reset condition ch 1 shall be one all the time (you can connect that the logic high in you logic)
2- changing the state of the (Reset counter ch 1)by using logic to change it is state from low to high
you just need to connect these two registers to a variables in your logic and just apply steps one and two
regards
Source:
Greetings
you can fiend attached PIC of the setting
Add new comment