Default ip address
Voted best answer
Hello,
Use TK212 cable and use IPConfig Tool for setting the IP address of the controller.
Follow steps:
Use COM4 of controller and click connect. And reset the controller by pinning the "INIT" on the front of controller and hold it till it gets reset.
Give the IP
You can start the IPConfig tool by:
Start | Programs | ABB Industrial IT 800xA | Engineering | Utilities | IPConfig
1. Connect your PC with the controller using a TK212 cable connected to serial port
on your PC and to the toolport (COM4) on the AC 800M controller.
2. Choose the COM port on your PC by click on “Settings”
3. Press “Connect”
The IPConfig status bar will change from Not Connected to Connecting.
4. Make a long (more than 3 seconds) Init of the controller, release the init button
when the Run LED start to blink.
After the systemreset
button has been pushed it takes approximately 10s before
IPConfig detects the system reset and the status bar changes to System reset
detected waiting for controller startup.
5. When IPConfig is connected the status bar will change to Connected.
6. To set the submask, you must enter advanced mode by choose “Settings” and
choose the “Advanced mode”.
7. Modify IP address, press “Set IP” and the text boxes will show the current
controller IP address settings.
When the new IP address has been stored successfully the status bar will show
“Controller IP configuration updated”.
Thanks
Answers
Hi
Refer below document
3BSE041880-xxx_en_AC_800M_Getting_Started.pdf
and search for IPconfig
Hi
Check this post and comments
http://www402.abbext.com/mobile/m/IP-...
Default ip is like 172.16.35.15
Use TK212 cable and use IPConfig Tool for setting the IP address of the controller.
Use COM4 of controller and click connect. And reset the controller by pinning the "INIT" on the front of controller and hold it till it gets reset.
You can start the IPConfig tool by:
Start | Programs | ABB Industrial IT 800xA | Engineering | Utilities | IPConfig
1. Connect your PC with the controller using a TK212 cable connected to serial port
on your PC and to the toolport (COM4) on the AC 800M controller.
2. Choose the COM port on your PC by click on “Settings”
3. Press “Connect”
The IPConfig status bar will change from Not Connected to Connecting.
4. Make a long (more than 3 seconds) Init of the controller, release the init button
when the Run LED start to blink.
After the systemreset
button has been pushed it takes approximately 10s before
IPConfig detects the system reset and the status bar changes to System reset
detected waiting for controller startup.
5. When IPConfig is connected the status bar will change to Connected.
6. To set the submask, you must enter advanced mode by choose “Settings” and
choose the “Advanced mode”.
7. Modify IP address, press “Set IP” and the text boxes will show the current
controller IP address settings.