ACS550 COMM PROFILE Perameter
Hi,
What I have to select in COMM PROFILE perameter in ACS550 drive (ABB DRIVES or GENERIC ) for Communication on Profibus network with 800xa system ?
What is the difference between two types?
How to Set Min and Max value for Speed referance in drive manually or by Abb800xa?
Answers
Hi,
I have used ABB DRIVES profile with RETA-02 module in ACS800 drive. I suggest you to download ACS550 drive firmware manual and you can find the required details in it, it would be available in ABB website. I found the following in ACS800 manual.
"The ABB Drives communication profile should be selected with type Nxxx fieldbus
adapter modules, and when the manufacturer-specific mode is selected (via the
PLC) with type Rxxx fieldbus adapter modules.
The Generic Drive profile is supported by type Rxxx fieldbus adapter modules only."