ac800f
I'm going to connect an ac800f controller to an existing rack system I/O cards (Freelance 2000) via CAN BUS.
Which type of PM802F or PM803F shall I select? Are those working properly?
FYI, I'm going to use CBF ver8.2 for this system.
Many thanks in advance.
Answers
Hello,
You can select any type PM 802/3F, Off course they work properly :)
however you need to use FI 810F module at F1 slot only with either of the controller you select, to communicate with rack modules.
Hi,
I would better go for the PM803F because it has a bigger memory (16 MB) that for sure can accommodate the existing rack system (usually use DCP02 or DCP10 CPU's with 8MB so if no exact info about used memory I would go for the upper one)