Hart - Enable Communication Error
I'm trying to enable the communication on Fieldbus management, However, It is saying that channel is not assigned as in the attachment even when I have done it. Am i missing something here ?
Answers
Hi!
Please check the setting "Tool routing" in the controller is enable.
Also, check that the services "OPC" and "FBB-OPC" are in service status.
For further information, please see the manual "3BDD011934-### X System 800xA Device Management 5.1 PROFIBUS and HART Configuration".
Hope it help.
Best regards
Can you check on the Fieldbus Management aspect of Modulebus that AI880 module is under it? Post the picture.
Hi,
Looks like the topology is corrupt.Kindly write to local supportline for FBBMergeTool which rectifies the corrupt topology.This is a licensed tool for the support will providethe password.
I have some problem how to solve this problem. Best regards
Add new comment