ABB ACS550 Drive communication profibus
Hi daniel ,
I required your help to communicate ABB Acs550 with 800xa Through profibus.From documents I knew that RPBA-01 required for Communicate Abb drive via profibus.
Under RPBA-01 Which PPO type I can add?
What is the diffrence between PPO -1, PPO-2, PPO-3 , PPO-4, PPO-5.
I required following parameter of drive On/Off Status, Local/remote Status, Fault Status and Current, SPeed. For controlling on/off cmd, Reset command . Analog output for speed control required.
Voted best answer
Hi
about RPBA-01 device, at the follow link you can find the manual of the unit:
https://library.e.abb.com/public/e237...
The PPO type choosing is depending on how many variables you want to exchange between drive and controller.
Hope this help you
Add new comment