AC500 PM573-ETH I can't login.
Answers
1. scan your IP address of your PLC through automation builder.
2.check your ETH cable
3.try to access the PLC through RS485 port then reset and check.
Hi
what version of Automation Builder / Control Builder are you using?
It's your first log to the cpu? This cpu is already running or not?
In Automation Builder you must activate the IP Scan Tool. During the scan the tool return the basic IP adress of the CPU, if the cpu is new - without any program inside.
When you have read the IP adress with the tool, you must set the Automation Builder suite - communication setup - as in the image below (adress indicate is for example):
Only after these steps you can login.
Very important: do not forget that if you provide more information about your problem, we will probably help you better.
Hope this help you
Hi
AFAIK, the access to the cpu is possible ONLY with Codesys with the classic series, such PM571-581 etc.
It's normal that with your PM573 the access is possible ONLY with Control Builder, because Codesys is a part of the suite.
You need to start before the Control Builder suite and then activate Codesys to have the access to the cpu.
Hope this help you
Hi
For login from Codesys, which configuration config?
Hi
If you start only Codesys, you need to config the communication parameter :
Online --> communication parameter as in the following image:
But if you have Control Builder, I do not understand why you want to use your cpu only with codesys