Monitoring hardware with SNMP
Hello,
I want to watch state of my Esxi server with SNMP. Setup of ESX seems to be ok.
I've read in the doc "Virtualization with VMWare vSpehere ESXi" (p.147) that the service "ABB PSNM trap receiver" must run.
This service does not exist on my node. How can I install this service ?
I tried to install "ABB PC, Network and Software Monitoring.msi" but service does not appear.
System : 800xA 6.0.3
ESXi : 6.5.0
Answers
First of all on 800xA v6.x do not install software manualy, but use the system configuration console instead. If you haven't loaded the system extension for ABB PC, Network and Software Monitoring please uninstall the software and use system configuration console to add the software and a new role to the system. Also esxi 6.5 is not yet supported as there are compatibilty issues with 800xA.
On you real question unfortunately I can not help.
Also notice you would need the system extension:
H160: PC, Network and Software Monitoring (3BSE078879R1)
Unfortunately it has quite a high price tag on it....
Hi,
I agree to WvanWees
For receiving ESXi traps, you should have PNSM software installed and check ABB PNSM trap Receiver service in Windows Services on PNSM server node
I used the system configuration console as you said and it works, the ABB PNSM Service has been created.
The manual installation is not a complete installation.
Thanks to all.
Add new comment