AC450, HMI 800xA
Dear Team,
We have AC450 which communicating with engineering station through MB300 but not comunicating with 800xA, only one node is not communicating. It is both communicating through RTA board.
Please support,
Answers
Did it work before? Can you post a screenshot from the control structure --> system status viewer. And the Mb300 node status from the control structure. Please provide some more information as your question leaves a lot of room to gues what is wrong.
Have you tried rebooting the server?
Is the 800xA rta connected trough an ethernet tranceiver, if yes replace that, as these brake quite often.
yes it was working before, MB300 which is in the rack is healthy but in the HMI it is as I have attached. control structure and status viewer is attached. We tried rebooting the server but nothing work. Ethernet transceiver already replaced.







Hi,
Did you reboot RTA board (PU410)? If not try this. You can do it from Control Structure.
Darek