Hi
Ist it possible to extend the live Trends and Eventlists on the productive System with the HistoryServer for 800xA Version 6.0.3.1?
Das anybody have one in central Europe?
See manual: 2PAA107563-600 B
Thanks Arno
Voted best answer
Yes, thats what it's build for. I assume you are using basic history. You can have both at the same time.
We use 800xA History several places (in england)
Pleace note the product did recieve several upgrade/bug fixes - So use 6.0.3 with History RU2.
The manuel you refer to is also rewised is now:
2PAA107563-600 D E en System 800xA 6.0 800xA History Administration and Configuration.
Answers
Do i have configure every single Signal or ist it like Audittrail with a Single Checkbox? I'm a confused about the License thing. We have around 20000 Tags with diffrent Alarms and Events. So i have to buy two of the 15,000 signals License?
Is maybe the IM a better and cheaper Solution if I would only extend the logs and the EventLists?
Is maybe the IM a better and cheaper Solution if I would only extend the logs and the EventLists?