ABB800M to Phoenix Contact Visu+ SCADA communication
Our customer has an AC800M ABB PLC controller using Citec Scada (xp version). Now we upgrade to Phoenix Contact Visu+ Scada, but we cannot communicate with the Visu+ due to communication protocol where the ABB800M is using MMS server.
Is there a way we can change the Com setting of ABB800M com protocol to be compatible with the Phoenix Contact Visu+?
Thank you
Is there a way we can change the Com setting of ABB800M com protocol to be compatible with the Phoenix Contact Visu+?
Thank you
Answers
You can use the AC800M opc server.
In addition to the previous answer, with just a few steps this is possible:
1. Install the ABB OPC server on the SCADA system
2. Connect to the controller
3. The OPC server needs some files, you can find them in your Control Builder project folder.
4. Connect the Phoenix Contact Visu+ Scada OPC client to the ABB server.
Good luck!
Add new comment