Error when plausibility button-field, Operation needs confimation is checked. Error: No confirm action configuered
In the button-field I checked "Operation needs confimation". When I want to plausibil the projekt I get an errormessage "No confirm action is configuered, but object needs confimation". What is wrong?
Answers
I guess this is related to Freelance graphics, double click on error message should bring pointer/cursor to error point.
Anyways it means check in button parameter,
variable <>value you need to select cancel confirm action
variable = value you need to select execute confirmation action, this depends on your logic requirement.
but setting this error should get disappear in plausibility check. please readh through operator station configuration manual or online help.
Hope this helps.
In freelance, if you select 'Operation needs confirmation' in button configuration, then in the same graphic page one more button(Confirm button) has to be defined by selecting 'Execute confirmed operation' in the Action type. So that if you click a button, then Confirm button will get activated to confirm execution of selected button action.