800-104 Communication Error PPCC link (5210)
Hi,
have ACS800-104-0460-5+E205+V991 and Communication Error PPCC link (5210).
Fiberoptic cables "OK"
RDCU-12C - "OK"
AINT-14C - "OK"
Flat Cables to IGBT - "OK"
IGBT - tested, - "OK"
Laptop with Drive Window woks with other tipe VFD.
Before do not have problem with ACS800-104-0580-7+C126+E205+V991.
Answers
It happen to me once - crossed by mistake fiberoptic cable between RMIO and AINT in ACS800-07.
Try with crossing of fiberoptic connectors - put Rx to Tx and Tx to Rx.
Is it power supply to RMIO OK?
03.19 - 4h -> Voltage Measurement Scaling error !! Contact ABB.
Could be defective AINT board or connection to the voltage measurement, check du/dt filter as well.
As per service instruction at 9-th year AINT flat cables and discharging resistors have to be replaced, each 6-th year should replace ALCL filter capacitor.