How many no of Modbus RTU slaves can be considered in a Modbus TCP/IP communication Card in AC 800 M controllers
As part of Modbus TCP/IP Card Sizing, I am considering 32 modbus RTU Slaves in a single Modbus TCP/IP Card through a single Modbus TCP/IP to serial Converter, Please confirm me is it with in the limit? what are the limitation are there other than the slave count?
Voted best answer
ABB recommends not to use more than 4 Modbus RTU slaves through single Modbus TCP/IP to serial converter.
Please see pg 93 of doc "3BSE035982-510_en_AC_800M_5.1_Communication_Protocols.pdf ".
However it can be increased depends on slave response time but 32 modbus RTU Slaves through single Modbus TCP/IP to serial converter seems to be not feasible.
Answers
Hi,
A Maximum of 70 Slave and 8 master units per CI867 ( on Ch1 and Ch2 together) can be used .
Please refer the Page no 178 for more information in 3BSE038018-510_-_en_System_800xA_5.1_System_Guide_Functional_Description[1]mann
ual .
Regards
Ravi kant Gupta