Why i can not use (PID Simple CC) with AC800M Compact
Greetings
I am trying to use a PID loop (PID Simple CC) block in my application program
I could not find it in the drop down list in the Editor
even i do connection it is library(Controlstandardlib1.4-7) to the application
I do the same for the (ControlBasiclib1.2-4) and i can use it is conrol blocks
Since my control station has no Real IO modules the using of the PID Loop in the control basic lib is no use
Kindly Advice
Regards
Voted best answer
Hi,
PIDSimpleCC is part of the Library ControlStandardLib.
Be aware, that this library has only Control Module Types, but no Function Block Types!
Control Moul Types can be used when programmining in ControlModule Language (but not in Programs) while Function Block Types can be used within Control Modules and Programs.
br
Reinhard
Answers
Hi,
PID Simple CC can be used in a time-critical task. Connect your application to that task and check whether you can add it.
Hello,
When you are trying to add PID Simple CC control module in your application, will you able to see ControlStandardlib at righthand side tab as shown below.
If yes then click controlStandrdlib then you can see all the controlmodules of that lib at left hand side tab.
To maintain continuity, copied reply from same previous question,
Amit ... Good day
As you can see in my question that i did do that step the lib is connected to the application
but i can not use the PID Simple CC in the application
kindly advice
Regards
Osama
Add new comment